A few notes on the EICR from my point of view
In the schedule of results (RCD column) there is a 30mA RCD listed under protecive devices, yet there is no disconnection rimes or functional test check
Item 3.4 is listed as a C1 - this would be the case if there is no earth and the power is on, the supply shows an external loop value of 0.11 so at works this would be a C3
The schedule also shows main gas and water bonding
4.18 - shows a C2- this box is usually ticked if the external earth is too high (such as a TT supply), the supply is listed as NOT TT, this should be listed as N/A
4.19 is N/A where it should be a C3 (no RCD additional protection)
6.1 indicates RCD protection in the bathroom - this is ticked and if this is the case then item 6.4 should be N/A
Section 5.12
The installer has indicated (again) there is RCD protection
5.11 - apparently all concealed cables are armour or in metal conduit etc (the wiring is listed as type A which is PVC twin and earth)
4.22 and 4.23 are ticked - apparently you have solar panels / generator which operates connected to the grid as well as not connected to the grid
4.20 - you have a surge protection device (SPD) in property (not likely as the fuse box has rewirable fuses)
There is other stuff, can you send a photo of the consumer unit area and post it here please?
In the schedule of results (RCD column) there is a 30mA RCD listed under protecive devices, yet there is no disconnection rimes or functional test check
Item 3.4 is listed as a C1 - this would be the case if there is no earth and the power is on, the supply shows an external loop value of 0.11 so at works this would be a C3
The schedule also shows main gas and water bonding
4.18 - shows a C2- this box is usually ticked if the external earth is too high (such as a TT supply), the supply is listed as NOT TT, this should be listed as N/A
4.19 is N/A where it should be a C3 (no RCD additional protection)
6.1 indicates RCD protection in the bathroom - this is ticked and if this is the case then item 6.4 should be N/A
Section 5.12
The installer has indicated (again) there is RCD protection
5.11 - apparently all concealed cables are armour or in metal conduit etc (the wiring is listed as type A which is PVC twin and earth)
4.22 and 4.23 are ticked - apparently you have solar panels / generator which operates connected to the grid as well as not connected to the grid
4.20 - you have a surge protection device (SPD) in property (not likely as the fuse box has rewirable fuses)
There is other stuff, can you send a photo of the consumer unit area and post it here please?