Yet another EICR......

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

    Yet another EICR......

    Have attached an EICR had done and looking for advice. Seems to be lots of further investigations and is a plastic consumer unit a C2 or C3.
    EICR is too big to attach apparently so have copied the relevant bits.

    C2'S

    7 Condition of enclosure(s) in terms of IP rating etc (416.2) Consumer unit mounted on wooden batten allowing cable entries on rear ( upper and lower surfaces ) to be accessible - no longer IP4X
    8 Condition of enclosure(s) in terms of fire rating etc (421.1.201; 526.5) - plastic CCU with openings for cable entry
    16 Open circuit for LINE conductors on circuit 3 ( ring final for sockets within flat ) - URGENT INVESTIGATION

    F1'S

    4 Confirmation of main protective bonding conductor sizes (544.1)
    5 Condition and accessibility of main protective bonding conductor/connections (543.3.2; 544.1.2)
    9 Presence of RCD six-monthly test notice at or near consumer unit/distribution board (514.12.2)
    15 Suitability of current-using equipment for particular position within the location (701.55) - location of bathroom fan directly above shower head ( < 0.5 m )
    17 Bathroom fan installed directly above shower head. Limited access to check it is suitable for location ( zone 2 ) - SELV ?
    20 Boiler feed from ring-final circuit of main flat ( not kitchen ring-final circuit nor separate supply ). Investigate source of wiring
    22 No accessible local isolation for each integrated kitchen appliances ( fridge, freezer, dishwasher, washing machine ). Access and verify connections to kitchen ring-final circuit.
    23 No accessible local isolation for cooker. Access and verify wiring accessory behind unit.
    24 Socket outlet behind wardrobe in front bedroom inaccessible at time of report




    #2
    Originally posted by madmaxwell View Post
    Have attached an EICR had done and looking for advice. Seems to be lots of further investigations and is a plastic consumer unit a C2 or C3.
    EICR is too big to attach apparently so have copied the relevant bits.

    C2'S

    7 Condition of enclosure(s) in terms of IP rating etc (416.2) Consumer unit mounted on wooden batten allowing cable entries on rear ( upper and lower surfaces ) to be accessible - no longer IP4X
    Seal with barrier such as intumescent expanding foam or silicone etc

    8 Condition of enclosure(s) in terms of fire rating etc (421.1.201; 526.5) - plastic CCU with openings for cable entry
    Not a problem if no thermal damage should be a C3
    16 Open circuit for LINE conductors on circuit 3 ( ring final for sockets within flat ) - URGENT INVESTIGATION
    This needs checked, about 1-2 hours work approx

    F1'S

    4 Confirmation of main protective bonding conductor sizes (544.1)
    If size cannot be confirmed continuity can be confirmed with wander lead and noted if fine or not

    5 Condition and accessibility of main protective bonding conductor/connections (543.3.2; 544.1.2)
    If size cannot be confirmed continuity can be confirmed with wander lead and noted if fine or not

    9 Presence of RCD six-monthly test notice at or near consumer unit/distribution board (514.12.2)
    Put a sticker on FFS

    15 Suitability of current-using equipment for particular position within the location (701.55) - location of bathroom fan directly above shower head ( < 0.5 m )
    Nonsense- fan is designed for use in bathroom (if not buy a new fan for £15 and you know complies and put it in)

    17 Bathroom fan installed directly above shower head. Limited access to check it is suitable for location ( zone 2 ) - SELV ?
    Nonsense- fan is designed for use in bathroom (if not buy a new fan for £15 and you know complies and put it in)

    20 Boiler feed from ring-final circuit of main flat ( not kitchen ring-final circuit nor separate supply ). Investigate source of wiring
    Not a departure

    22 No accessible local isolation for each integrated kitchen appliances ( fridge, freezer, dishwasher, washing machine ). Access and verify connections to kitchen ring-final circuit.
    Poor workmanship, not dangerous- socket may be in cupboard or under unit

    23 No accessible local isolation for cooker. Access and verify wiring accessory behind unit.
    Poor workmanship, not dangerous- socket may be in cupboard or under unit

    24 Socket outlet behind wardrobe in front bedroom inaccessible at time of report
    Note as limitation on cert- that's what they are there for.

    See above comments in RED

    Comment


      #3
      Hum

      so there are no IP ratings required for the rear of a fuseboard

      other than that I quite agree with baldelectrician

      Comment


        #4
        So am i being ripped off. Should i have another EICR DONE.He has quoted £850 for new consumer unit and carry out the further investigations and has said it will take 3 days

        Baldelectrician....what do you mean by not a departure re number 20

        Comment


          #5
          Originally posted by madmaxwell View Post
          So am i being ripped off. Should i have another EICR DONE.He has quoted £850 for new consumer unit and carry out the further investigations and has said it will take 3 days

          Baldelectrician....what do you mean by not a departure re number 20
          Those prices are extortionate.

          Where in the UK are you?

          Comment


            #6
            newcastle.....How do you find an electrician that wont rip you off.

            Comment


              #7
              Originally posted by madmaxwell View Post
              newcastle.....How do you find an electrician that wont rip you off.
              ask friends or neighbours ...

              do you use Nextdoor ?

              people often ask for recommendations for all types of trades on there .... and I get quite a lot of enquires this way


              please don’t tar us all with that brush

              Comment


                #8
                Originally posted by madmaxwell View Post
                So am i being ripped off. Should i have another EICR DONE.He has quoted £850 for new consumer unit and carry out the further investigations and has said it will take 3 days

                Baldelectrician....what do you mean by not a departure re number 20
                I mean it is not against the regulations to have a gas heating system powered from a socket circuit, the heat is being done by the gas so the additional load on the socket circuit is negligible