    GU10 spotlights with no earth


    What's the EICR situation where GU10 Spotlights which have no earth are fitted?

    68666230.jpg

    #2
    Same as every other light fitting with no earth I would think. It's quite normal.

    Comment


      #3
      So would be ok and pass?

      Comment


        #4
        Originally posted by Chester Perry View Post
        So would be ok and pass?
        No, and yes

        The light may not need an earth but the cables termination point (the joint box) should have an earth

        In other words there should be an earth at each accessory, it is then up to the installer to connect it or not as required

        No cpc continuity and metal unearthed light fittings would fail an EICR

        No earth at the termination where there are lights which do not require an earth would be a C3

        Comment