  • Electrical Safety Check - Criteria?

    Hi, I am a new landlord renting an ex council property for the first time in Scotland and would be very grateful for some technical advice if you can spare the time.

    I have carried out a Landlords electrical safety check on all the electrical appliances in the flat and also the whole flats electrical circuitry has been checked. This check was carried out by an NICEC electrician.

    My problem is that during the check it was discovered that there was no earth supplied to the flat! The power supply is provided to the houses in the street by means of overhead cables rather than underground cables. In the place of the normal earth, we have an RCD trip switch which (I understand, as a complete novice) trips in the event of an overload. He then gave me a report that said the flat had failed the safety check due to the earth problem.

    The electrician said that in order to provide me with a report saying that the flat was electrically safe I would need to have an earth supplied to the flat (at no doubt great expense). I called in Scottish power (electricity provider) and they said that the supply was perfectly safe with the rcd switch but if I needed the earth installed anyway there was a long lead time.

    AT LONG LAST - MY QUESTION : Is the NICEC electrician correct in that even with the RCD switch installed, legally the flat is still unsafe (the previous owners have lived in the flat for five years with no problems)? Are there any other standards other than those used by NICEC which accept the use of an RCD as normal practice? I don't want to endanger anyone but feel that this might be a money making exercise on the part of the electrician. Any thoughts would be very welcome. Thanks.

  • #2
    This sounds more of a techie question for sparkies then a residental question. Basically you dont need a certificate for any existing electrical work, you only need a certificate for new work carried out within certain criteria, do a search for Part P on this forum. However, you have been prudent and carried out a check and found a problem therefore you will probably have to act on it. I allways go on the www.diynot.com forums for anything to do with techie stuff.

    Hope this helps

    Comment


    • #3
      Daza,

      thanks for your advice. I give that a try.

      Comment


      • #4
        Earth

        I'd strongly suggest you ask your query on the uk.d-i-y usenet newsgroup (at http://groups.google.co.uk/group/uk.d-i-y?lnk=lr&hl=en if you don't have an off-line newsfeed) - it's extremely active, full of experts, and I'm sure someone there will have the answer. Alternatively, try the 'talk' forums on www.screwfix.com.

        I'd be fairly sure that having RCDs doesn't circumvent the need for an earth, and that your sparks is correct, but don't quote me on that!

        Comment


        • #5
          Earthing

          It looks like you have what is called a TT supply. The responsibility for providing the earth is yours. To ensure the RCD operates correctly there must be a maximum impedance of 1666 ohms to earth. To ensure safe operation the impedance should be as low as possible, say 10 ohms. Where the supply is TT an RCD is mandatory
          The best configuration is a split load consumer unit with a 100mA time delayed RCD main incomer protecting lighting fridge etc. This 100mA unit is upstream of a 30mA RCD protecting sockets etc. This configuration gives overall protection. The equipment on sockets is more likely to cause a problem and would trip the 30mA RCD whilst the lighting circuits remain on.
          Installation of an earth rod should not cost a lot (rod about £10). The rod is hammered into the soil as close as possible to the consumer unit. Check there are no underground services before starting. Your electrician should be able to carry out the work in a few hours assuming your consumer unit does not need changing.

          Comment


          • #6
            where to go from here

            Kelly build has answered you. Without being too technical, get your niceic fellow to fit an earth rod (a TT system) is correctly in place. When the loop impedance is measured, the voltage should not go over 50Volts. let him sort the rcd thing out for you. This is a code 1 failure "requires urgent attention" as listed on page 2 of the report. this is a directive from the IEE not the NICEIC. he can only fail the installation on breech of regulations in BS7671, which he has correctly identified.

            Be under no illusion, the whoever was there before had no problems, therefore it should be safe! this is a big misconception often suggested by our customers. A bit like a seatbelt.... it is there for when you need it... it doesn't stop the crash.
            Hope this helps

            Elektratek
            Regards

            Elektratek Ltd.


            For information only. No responsability is taken for any actions performed by use of this posted message.

            Comment

            Latest Activity

            Collapse

            • Deposit at the end of AST. Also, quiet enjoyment.
              scooter08
              Q1 – Where is the rented property located (England / Wales / Scotland / N Ireland)?
              England

              Q2 – What type of Tenancy Agreement (TA) is this e.g. sole tenant / multiple tenant / room only?
              AST

              Q3 – What date did current TA start dd/mm/yy?
              12/04/2015
              ...
              21-07-2017, 15:06 PM
            • Reply to Deposit at the end of AST. Also, quiet enjoyment.
              scooter08
              Thanks for the reply jp....
              21-07-2017, 18:32 PM
            • Reply to Deposit at the end of AST. Also, quiet enjoyment.
              jpkeates
              Makes sense - if the tenancy agreement doesn't say you have to let him and a surveyor in, his only right of access is with 24 hours written notice for the purpose of viewing the "condition and state of repair" of the property.

              So you can simply decline or make your point.
              ...
              21-07-2017, 18:23 PM
            • Reply to Deposit at the end of AST. Also, quiet enjoyment.
              scooter08
              I'm not trying to claim for breach of quiet enjoyment. He wants to be in again with a surveyor to use his property as security for something. I am going to let him I just want to remind him and have all the facts. Sorry if I didn't explain it right.

              Only claiming for the non protection...
              21-07-2017, 18:08 PM
            • Reply to Deposit at the end of AST. Also, quiet enjoyment.
              scooter08
              I pay the council tax, yes it is mortgaged. As far as I know he isn't pretending to live him and his family live in another house a few streets away....
              21-07-2017, 18:01 PM
            • HMO under Commercial Lease & homeowner wants to sell
              bald555
              Long story short, someone I know (not close) needed money, I gave him 12 months reduced rent upfront to help him out and put a commercial lease on his HMo with right to sublet etc (my tenants).

              Few months in and his money problems are worse and the bank (and others) pressuring him to sell...
              21-07-2017, 16:58 PM
            • Reply to HMO under Commercial Lease & homeowner wants to sell
              bald555
              and yes, there is a mortgage...
              21-07-2017, 17:44 PM
            • Reply to Deposit at the end of AST. Also, quiet enjoyment.
              jpkeates
              Harassment is way more than a breach of quiet enjoyment, there has to be a level of distress in the harassed person.

              A retrospective claim for breach of quiet enjoyment is probably a non-starter - breach of quiet enjoyment is part of the kitchen sink people throw when they're claiming compensation...
              21-07-2017, 17:43 PM
            • Reply to Deposit at the end of AST. Also, quiet enjoyment.
              Wright76
              And although as jpkeates suggests you have a right to turn them away and force a court order, this does not mean they have breached your right to quiet enjoyment.

              It means you are refusing to honour your AST and the landlord Is forced to apply to court to make you legally comply. Again,...
              21-07-2017, 17:35 PM
            • Reply to HMO under Commercial Lease & homeowner wants to sell
              bald555
              Many thanks for the reply. Yes, my company has leased the HMO in question under commercial lease but it's not registered at land registry as it's only a 12 month lease.

              Tenants are friends so less of am issue as such but they'll be outside of their 6 months by the time of any would be...
              21-07-2017, 17:31 PM
            Working...
            X